Equipped To Survive Equipped To Survive® Presents
The Survival Forum
Where do you want to go on ETS?

Page 2 of 2 < 1 2
Topic Options
#246342 - 05/27/12 03:11 PM Re: Turning a cheap APC UPS into a monster UPS [Re: SARbound]
dougwalkabout Offline
Crazy Canuck
Carpal Tunnel

Registered: 02/03/07
Posts: 3240
Loc: Alberta, Canada
I think it's a worthwhile experiment. The wiring is dirt simple, and the batteries run in the same voltage range. A deep-cycle battery is not necessarily required. It would certainly be useful in a longer-term power outage for lights and laptops; but don't expect to run a refrigerator.

There's no reason why a small solar panel (up to 5 watts) can't be used as a trickle charger while connected to the UPS. But pre-charge the battery before connecting, and shut down the UPS before using a line-powered battery charger.

Be aware that some UPS units, APC in particular, will not fire up on the inverter side after the battery has discharged. They have to see line (grid) voltage.

Risk: this depends on where you plan to use it.

I would never put a setup like this in a house. If something goes wrong, you are liable. (And insurance will probably laugh at you if try to make a claim.)

However, for a small off-grid outbuilding, it would be less of a risk. The battery and inverter should both be outside, in separate, weather resistant, ventilated enclosures.

The primary danger is a short across the battery terminals or the wiring. There is a lot of energy in a larger battery -- enough to start a fire or damage the battery in a dangerous way.

If you decide to build it:
- use very heavy wire from the battery to the UPS, and as short a run as possible
- install a 12V fuse or circuit breaker right at the battery to protect against a short circuit
- double-check polarity
- use good mechanical connections, with lots of wire overlap; spring-loaded clips are a recipe for trouble
- heavily insulate all connections
- monitor closely for overheating and odd smells

Personally, I would only use a hotwired setup under direct supervision, and only for light loads.

Top
#246345 - 05/27/12 03:21 PM Re: Turning a cheap APC UPS into a monster UPS [Re: SARbound]
adam2 Offline
Addict

Registered: 05/23/08
Posts: 483
Loc: Somerset UK
I have done this many times, and it should be safe provided that proper care is taken.
The external battery must be the same voltage as the original internal battery, normally 12 volts for the smaller units, 24 volts for larger ones, and more than 24 for very large ones.

Remember that the original battery was enclosed within the UPS and not readily touched, therefore the battery terminals MAY NOT be isolated from the line supply. That is a potentialy fatal line voltage shock could be received from the 12 volt battery leads.
Even if testing shows that the battery leads are isolated from the line supply, do not count on this !
UL or equivalent listing sets very strict standards for isolating line voltage from low voltage connections that can be touched, for example on consumer electronics.
These standards DO NOT apply to UPS units with internal batteries, since when used as intended the battery terminals cant be touched.
I would put the external battery in a large plastic crate with the lid secured to protect the terminals form touch.

The cable to the external battery needs for very thick and not too long. Suggest at least one size larger than the internal battery leads.

Fit an external fuse as close as possible to one battery terminal, size this at about 150% of the running current.

Remember that the inverter may only be designed for short term use, limited by the run time of the small internal battery, and may be killed by overheating if run continually at full power.
If extending the run time with an external battery, I would limit the load to less than 50% of the rating.

The external battery will take longer to charge.

I would accept this and not try and connect any other charger.

The powerchute shutdown software should still work to an extent, but dont count on it being accurate, I dont use it.

The UPS in my office is an APC smart UPS, 700 VA and is intended to use an internal battery of 24 volts 7 A/H.
I have fitted an external battery of 200 A/H and it works just fine, and has seen regular use for years.
The load varies but is typicly about 250 watts
desktop PC, flourescent light, desk fan, router, cellphone charger, Moterola radio charger, inkjet printer.

It certainly ran for a 9 hour working day without problems.

At my Mothers home I installed a 3,000VA UPS with a large external battery bank.
That runs basic lighting, fridge, freezer, TV, cordless phone base unit, cellphone charger, and so on on for several days.
The actual load is probably only about 100 watts average, 500 watts maximum.
I selected a 3,000 VA UPS to ensure that it will start the fridege and freezer.
Computer type UPS units are not ideal for starting motors, and as a crude guide the UPS needs to be rated at TEN times the rating of the connected motor load.
200 watt fridge=min 2,000VA UPS.

Top
Page 2 of 2 < 1 2



Moderator:  Alan_Romania, Blast, chaosmagnet, cliff 
November
Su M Tu W Th F Sa
1 2
3 4 5 6 7 8 9
10 11 12 13 14 15 16
17 18 19 20 21 22 23
24 25 26 27 28 29 30
Who's Online
1 registered (Ren), 891 Guests and 17 Spiders online.
Key: Admin, Global Mod, Mod
Newest Members
Aaron_Guinn, israfaceVity, Explorer9, GallenR, Jeebo
5370 Registered Users
Newest Posts
Leather Work Gloves
by dougwalkabout
11/16/24 05:28 PM
Satellite texting via iPhone, 911 via Pixel
by Ren
11/05/24 03:30 PM
Emergency Toilets for Obese People
by adam2
11/04/24 06:59 PM
For your Halloween enjoyment
by brandtb
10/31/24 01:29 PM
Chronic Wasting Disease, How are people dealing?
by clearwater
10/30/24 05:41 PM
Things I Have Learned About Generators
by roberttheiii
10/29/24 07:32 PM
Gift ideas for a fire station?
by brandtb
10/27/24 12:35 AM
Newest Images
Tiny knife / wrench
Handmade knives
2"x2" Glass Signal Mirror, Retroreflective Mesh
Trade School Tool Kit
My Pocket Kit
Glossary
Test

WARNING & DISCLAIMER: SELECT AND USE OUTDOORS AND SURVIVAL EQUIPMENT, SUPPLIES AND TECHNIQUES AT YOUR OWN RISK. Information posted on this forum is not reviewed for accuracy and may not be reliable, use at your own risk. Please review the full WARNING & DISCLAIMER about information on this site.