Originally Posted By: bws48
Originally Posted By: ILBob
Re: electrical inspectors and generators

There are specific ways that loads are to be calculated according to the NEC. You have to use a NEC approved way when you install a generator.

In neither case are you required to consider every circuit that has a 15A outlet on it as a 15A load. If I recall correctly, they are generally calculated at 180VA per receptacle. Some of them don't have to be counted at all, while those dedicated to a specific purpose have to be considered at full load.

The calculations are fairly straightforward if you are used to them but are often daunting for the uninitiated.


No doubt.

I wonder if these calculations require actually looking at what is on each circuit?

Our inspector came in, looked at: 1) the amps of each of the circuits going to the sub-panel, 2) the size of the breaker sending the power to the sub-panel, 3) the sub-panel, and 4) the size of the generator.

I'm happy we passed. smile

I've often found that, in theory, theory and practice are the same, but that in practice, they are not. grin


None of the stuff mentioned matters much as far as the code goes for sizing the generator. Some of it matters for other things though.

The size of the CB on the branch circuits has close to nothing to do with sizing any feeder, including generators.

The only outlets where an actual load is considered are those dedicated to a specific item such as a refrigerator. If it is a dedicated circuit the actual load is taken into consideration.

It is possible that he looked at it and realized that your generator was more than adequately sized and just never looked any farther. Most likely the contractor supplied load calculations so he never looked at the actual load.
_________________________
Warning - I am not an expert on anything having to do with this forum, but that won't stop me from saying what I think. smile

Bob